ufkyldrm
Joined: 21 May 2018 Posts: 27
|
Modbus RTU communication problem on specific device. |
Posted: Fri Jul 27, 2018 11:14 am |
|
|
Hi guys.
This device has modbus rtu protocol but I can't read its register values.
its communication datasheet.
https://www.dosyaupload.com/dZt4
I tried it with modbus poll or Kepware Opc server... As I said with these softwares i got what I want, up to now. These softwares have a search function for devices which has modbus rtu. My opinion, it is not parameter issue.
I there any way to get value from this device, maybe with pic?
Any advice? |
|
|
Ttelmah
Joined: 11 Mar 2010 Posts: 19549
|
|
Posted: Fri Jul 27, 2018 11:22 am |
|
|
Triple check your communication parameters. Probably something like incorrect parity.
Unless you are actually using a PIC with CCS, this is off topic here. |
|
|
Jerson
Joined: 31 Jul 2009 Posts: 125 Location: Bombay, India
|
|
Posted: Fri Jul 27, 2018 10:09 pm |
|
|
First confirm using a software as suggested in the linked manual. If you are convinced there is no problem with the hardware, only then should you try with a PIC.
Probably wrong communication parameters (software shows correct should be 9600-N-8-1) may be the cause for no communication.
Since it is RS485, check the connections of your D+ D- lines as well. |
|
|
|